Jim, to answer this question, you also need to know the total length
of the wire run.
The resistivity (rho) of any material is a temperature dependent variable,
but the variance is small, and values for many materials at 20 degrees C are
available on the internet. A quick search provides the resistivity value
for copper as 1.724E-8 ohm*meters.
Resistance, resistivity, length and cross-sectional area are related by the
equation
R = (rho * l )/A
Voltage, current and resistance are related by the equation
V=I*R
Combining the two, and rearranging for A gives
A = (I * rho * l ) / V
Now, it is important to note that the V above is not your nominal operating
voltage, but rather a voltage corresponding to the acceptable voltage drop in
the wire. Many electrical codes give this as around 2% of the nominal
voltage, so for a 36V system that would be 0.72 V. You didn't provide a
wire length, but for the purpose of discussion, for a 10 meter wire, you
have
A = (150 * 1.724E-8 * 10) / 0.72 = 3.6E-5 m^2, or 36 mm^2. The
corresponding AWG wire gauge is about 2 AWG.
This is large, but this would be necessary if you were running at full
power continuously, and could not tolerate voltage drops higher than
0.72V. Provided you stay within safety limits (i.e. the isolation
voltage limit of the wire insulation), and can tolerate more heat, and more
voltage drop in the wire at maximum current, you can derate this to be a more
appropriate fit to the expected continuous load.
-Sean
On Jan 15, 2009, kocpnt@tds.net wrote:
Hi All,
I am looking for advice. I am looking for the
proper size of copper wire to power my sub.
This wire will go from the batteries and at
maximum draw will need to handle about 150 amps total load at 36 volts DC. I
realize that there places to look for this, but felt that the experienced
people in the community might have some good insights!
Thanks in advance,
Jim
K
************************************************************************
************************************************************************
************************************************************************ The
personal submersibles mailing list complies with the US Federal CAN-SPAM Act
of 2003. Your email address appears in our database because either you, or
someone you know, requested you receive messages from our organization. If you
want to be removed from this mailing list simply click on the link below or
send a blank email message to: removeme-personal_submersibles@psubs.org
Removal of your email address from this mailing list occurs by an automated
process and should be complete within five minutes of our server receiving
your request. PSUBS.ORG PO Box 53 Weare, NH 03281 603-529-1100
************************************************************************
************************************************************************
************************************************************************